Lights won’t work on dimmer
I just installed some recessed lighting in my basement and I can’t get the circuit to work properly.
The installation was: feed to multiple lights to dimmer switch. I used 14/2 for everything except from the last light to the dimmer switch, which I used 14/3. Only the last light dims and the other lights only stay on
Is my issue that I should’ve used 14/3 for everything or something wrong with the wiring?
lighting
add a comment |
I just installed some recessed lighting in my basement and I can’t get the circuit to work properly.
The installation was: feed to multiple lights to dimmer switch. I used 14/2 for everything except from the last light to the dimmer switch, which I used 14/3. Only the last light dims and the other lights only stay on
Is my issue that I should’ve used 14/3 for everything or something wrong with the wiring?
lighting
It sounds like maybe you need neutral - and therefore 14/3 - at the dimmer, in which case it maybe should have been 14/3 the whole way. But not very clear. Please provided, if you can: model # of dimmer switch, picture of wiring at last light (14/2 & 14/3), picture of wiring at dimmer switch.
– manassehkatz
2 hours ago
The switch is Halo LED SAL06P. I have the neutral unconnected since the switch says it doesn’t need a neutral with the black wire on top and red wire on bottom of the right hand side. From the switch, it’s to the last light in the chain where I have the neutrals together, the grounding together, the red to the light and the black from the incoming 14/2 and 14/3 together like I’ve seen in some diagrams online. All the other lights are setup so that all the whites are together, blacks are together, and grounding together.
– prchick1984
1 hour ago
add a comment |
I just installed some recessed lighting in my basement and I can’t get the circuit to work properly.
The installation was: feed to multiple lights to dimmer switch. I used 14/2 for everything except from the last light to the dimmer switch, which I used 14/3. Only the last light dims and the other lights only stay on
Is my issue that I should’ve used 14/3 for everything or something wrong with the wiring?
lighting
I just installed some recessed lighting in my basement and I can’t get the circuit to work properly.
The installation was: feed to multiple lights to dimmer switch. I used 14/2 for everything except from the last light to the dimmer switch, which I used 14/3. Only the last light dims and the other lights only stay on
Is my issue that I should’ve used 14/3 for everything or something wrong with the wiring?
lighting
lighting
asked 2 hours ago
prchick1984prchick1984
61
61
It sounds like maybe you need neutral - and therefore 14/3 - at the dimmer, in which case it maybe should have been 14/3 the whole way. But not very clear. Please provided, if you can: model # of dimmer switch, picture of wiring at last light (14/2 & 14/3), picture of wiring at dimmer switch.
– manassehkatz
2 hours ago
The switch is Halo LED SAL06P. I have the neutral unconnected since the switch says it doesn’t need a neutral with the black wire on top and red wire on bottom of the right hand side. From the switch, it’s to the last light in the chain where I have the neutrals together, the grounding together, the red to the light and the black from the incoming 14/2 and 14/3 together like I’ve seen in some diagrams online. All the other lights are setup so that all the whites are together, blacks are together, and grounding together.
– prchick1984
1 hour ago
add a comment |
It sounds like maybe you need neutral - and therefore 14/3 - at the dimmer, in which case it maybe should have been 14/3 the whole way. But not very clear. Please provided, if you can: model # of dimmer switch, picture of wiring at last light (14/2 & 14/3), picture of wiring at dimmer switch.
– manassehkatz
2 hours ago
The switch is Halo LED SAL06P. I have the neutral unconnected since the switch says it doesn’t need a neutral with the black wire on top and red wire on bottom of the right hand side. From the switch, it’s to the last light in the chain where I have the neutrals together, the grounding together, the red to the light and the black from the incoming 14/2 and 14/3 together like I’ve seen in some diagrams online. All the other lights are setup so that all the whites are together, blacks are together, and grounding together.
– prchick1984
1 hour ago
It sounds like maybe you need neutral - and therefore 14/3 - at the dimmer, in which case it maybe should have been 14/3 the whole way. But not very clear. Please provided, if you can: model # of dimmer switch, picture of wiring at last light (14/2 & 14/3), picture of wiring at dimmer switch.
– manassehkatz
2 hours ago
It sounds like maybe you need neutral - and therefore 14/3 - at the dimmer, in which case it maybe should have been 14/3 the whole way. But not very clear. Please provided, if you can: model # of dimmer switch, picture of wiring at last light (14/2 & 14/3), picture of wiring at dimmer switch.
– manassehkatz
2 hours ago
The switch is Halo LED SAL06P. I have the neutral unconnected since the switch says it doesn’t need a neutral with the black wire on top and red wire on bottom of the right hand side. From the switch, it’s to the last light in the chain where I have the neutrals together, the grounding together, the red to the light and the black from the incoming 14/2 and 14/3 together like I’ve seen in some diagrams online. All the other lights are setup so that all the whites are together, blacks are together, and grounding together.
– prchick1984
1 hour ago
The switch is Halo LED SAL06P. I have the neutral unconnected since the switch says it doesn’t need a neutral with the black wire on top and red wire on bottom of the right hand side. From the switch, it’s to the last light in the chain where I have the neutrals together, the grounding together, the red to the light and the black from the incoming 14/2 and 14/3 together like I’ve seen in some diagrams online. All the other lights are setup so that all the whites are together, blacks are together, and grounding together.
– prchick1984
1 hour ago
add a comment |
4 Answers
4
active
oldest
votes
According to the manual, for a single switch (as opposed to a a 3-way switch, which would require another wire and another (ordinary, non-dimmable) 3-way switch), the configuration is very simple (ignoring grounds, which should all be connected together everywhere):
- Top right screw = Black = Hot - this should go directly back to the panel
- Bottom right screw = Yellow = Switched Hot - this should go to the light(s)
- The "far side" of the lights goes to Neutral
With a single fixture this is straightforward:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/2 from light to switch at the light:
- Connect black hot to the first cable's black hot
- Connect white (="yellow") switched hot to the other side of the light.
14/2 from light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect white switched hot to lower right (= yellow according to the instructions)
Note that yellow is a typical "switched hot" color (could be red or blue or anything else except black, which is traditionally hot, white & gray, which are only neutral, or green, which is only ground). However, 14/2 cable only comes in black/white, so if you have the hot function in the cable then that gets black and switched hot or neutral gets white. Alternatively, if you have neutral function in the cable then that gets white and hot or switched hot gets black. So in this case, you use white as switched hot and then mark it with yellow tape to indicate that it is actually the switched hot.
This conveniently ignores that current code requires a neutral in the switch box, just in case you need it later. But hang on...
That gets one light working. But you have more than one. Now you need another wire. == 14/3.
The problem is you need to have two wires going between all the lights: switched hot and neutral. And you need another wire, not connected to any lights, for hot to get to the switch. With only one light, we cheat a little (except that neutral should be in the switch box) because there is no "carry neutral along to the next light" since there is only one light. But with multiple lights that doesn't work. So now you replace the 14/2 from the first light through all the other lights to the switch with 14/3. That 14/3 will be black/white/red. As described above, whenever possible black = hot and white = neutral. So that leaves red = switched hot. Here we go:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/3 from first light to second light, at the first light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the other side of the light.
14/3 from first light to second light, at the second light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the previous cable's red switched hot and to the other side of the light. This actually means use a wire nut to connect the reds from the two cables plus a pigtail to the light.
All the later lights use that same setup: blacks together, whites together + light, reds together + light.
14/3 from last light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect red switched hot to lower right (= yellow according to the instructions)
- Cap the white neutral with a wire nut
Now you have all the lights working and you have neutral in the box in case you need it in the future.
add a comment |
So here are the wires you need.
- ground from supply to every lamp and switch. Ground must be green, green/yellow, or bare.
- neutral from supply to every lamp and switch. Neutral must be white.
- always-hot from the power supply to the switch. Always-hot is preferably black.
- switched-hot from the switch to every lamp. Switched-hot is ideally red, but can be black if the black wire is available.
As you can see, since power enters the opposite end from the switch, you need to carry "always-hot" all the way. You also need to carry "neutral" all the way. Then, if you want the lights to be switched, you need to carry switched-hot all the way back from the switch to the first lamp.
The lamp's hot wire is black. You can hook it to always-hot if you want it always-on, but if you want it switched, I suggest hooking it to switched hot.
So yeah, you need /3 cable starting at the first lamp.
add a comment |
You need 14/3 between the lights
The reason why the lights are stuck ON is because they were wired directly between always-hot and neutral. Since you need to bring switched-hot back to all the lights in order for the switch to control them, you'll need to replace the 14/2 between the lights with 14/3.
add a comment |
That’s what I was afraid of. Looks like I’ll be practicing my electrical wiring skills some more
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
add a comment |
Your Answer
StackExchange.ready(function() {
var channelOptions = {
tags: "".split(" "),
id: "73"
};
initTagRenderer("".split(" "), "".split(" "), channelOptions);
StackExchange.using("externalEditor", function() {
// Have to fire editor after snippets, if snippets enabled
if (StackExchange.settings.snippets.snippetsEnabled) {
StackExchange.using("snippets", function() {
createEditor();
});
}
else {
createEditor();
}
});
function createEditor() {
StackExchange.prepareEditor({
heartbeatType: 'answer',
autoActivateHeartbeat: false,
convertImagesToLinks: false,
noModals: true,
showLowRepImageUploadWarning: true,
reputationToPostImages: null,
bindNavPrevention: true,
postfix: "",
imageUploader: {
brandingHtml: "Powered by u003ca class="icon-imgur-white" href="https://imgur.com/"u003eu003c/au003e",
contentPolicyHtml: "User contributions licensed under u003ca href="https://creativecommons.org/licenses/by-sa/3.0/"u003ecc by-sa 3.0 with attribution requiredu003c/au003e u003ca href="https://stackoverflow.com/legal/content-policy"u003e(content policy)u003c/au003e",
allowUrls: true
},
noCode: true, onDemand: true,
discardSelector: ".discard-answer"
,immediatelyShowMarkdownHelp:true
});
}
});
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
var $window = $(window),
onScroll = function(e) {
var $elem = $('.new-login-left'),
docViewTop = $window.scrollTop(),
docViewBottom = docViewTop + $window.height(),
elemTop = $elem.offset().top,
elemBottom = elemTop + $elem.height();
if ((docViewTop elemBottom)) {
StackExchange.using('gps', function() { StackExchange.gps.track('embedded_signup_form.view', { location: 'question_page' }); });
$window.unbind('scroll', onScroll);
}
};
$window.on('scroll', onScroll);
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
StackExchange.ready(
function () {
StackExchange.openid.initPostLogin('.new-post-login', 'https%3a%2f%2fdiy.stackexchange.com%2fquestions%2f157184%2flights-won-t-work-on-dimmer%23new-answer', 'question_page');
}
);
Post as a guest
Required, but never shown
4 Answers
4
active
oldest
votes
4 Answers
4
active
oldest
votes
active
oldest
votes
active
oldest
votes
According to the manual, for a single switch (as opposed to a a 3-way switch, which would require another wire and another (ordinary, non-dimmable) 3-way switch), the configuration is very simple (ignoring grounds, which should all be connected together everywhere):
- Top right screw = Black = Hot - this should go directly back to the panel
- Bottom right screw = Yellow = Switched Hot - this should go to the light(s)
- The "far side" of the lights goes to Neutral
With a single fixture this is straightforward:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/2 from light to switch at the light:
- Connect black hot to the first cable's black hot
- Connect white (="yellow") switched hot to the other side of the light.
14/2 from light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect white switched hot to lower right (= yellow according to the instructions)
Note that yellow is a typical "switched hot" color (could be red or blue or anything else except black, which is traditionally hot, white & gray, which are only neutral, or green, which is only ground). However, 14/2 cable only comes in black/white, so if you have the hot function in the cable then that gets black and switched hot or neutral gets white. Alternatively, if you have neutral function in the cable then that gets white and hot or switched hot gets black. So in this case, you use white as switched hot and then mark it with yellow tape to indicate that it is actually the switched hot.
This conveniently ignores that current code requires a neutral in the switch box, just in case you need it later. But hang on...
That gets one light working. But you have more than one. Now you need another wire. == 14/3.
The problem is you need to have two wires going between all the lights: switched hot and neutral. And you need another wire, not connected to any lights, for hot to get to the switch. With only one light, we cheat a little (except that neutral should be in the switch box) because there is no "carry neutral along to the next light" since there is only one light. But with multiple lights that doesn't work. So now you replace the 14/2 from the first light through all the other lights to the switch with 14/3. That 14/3 will be black/white/red. As described above, whenever possible black = hot and white = neutral. So that leaves red = switched hot. Here we go:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/3 from first light to second light, at the first light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the other side of the light.
14/3 from first light to second light, at the second light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the previous cable's red switched hot and to the other side of the light. This actually means use a wire nut to connect the reds from the two cables plus a pigtail to the light.
All the later lights use that same setup: blacks together, whites together + light, reds together + light.
14/3 from last light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect red switched hot to lower right (= yellow according to the instructions)
- Cap the white neutral with a wire nut
Now you have all the lights working and you have neutral in the box in case you need it in the future.
add a comment |
According to the manual, for a single switch (as opposed to a a 3-way switch, which would require another wire and another (ordinary, non-dimmable) 3-way switch), the configuration is very simple (ignoring grounds, which should all be connected together everywhere):
- Top right screw = Black = Hot - this should go directly back to the panel
- Bottom right screw = Yellow = Switched Hot - this should go to the light(s)
- The "far side" of the lights goes to Neutral
With a single fixture this is straightforward:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/2 from light to switch at the light:
- Connect black hot to the first cable's black hot
- Connect white (="yellow") switched hot to the other side of the light.
14/2 from light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect white switched hot to lower right (= yellow according to the instructions)
Note that yellow is a typical "switched hot" color (could be red or blue or anything else except black, which is traditionally hot, white & gray, which are only neutral, or green, which is only ground). However, 14/2 cable only comes in black/white, so if you have the hot function in the cable then that gets black and switched hot or neutral gets white. Alternatively, if you have neutral function in the cable then that gets white and hot or switched hot gets black. So in this case, you use white as switched hot and then mark it with yellow tape to indicate that it is actually the switched hot.
This conveniently ignores that current code requires a neutral in the switch box, just in case you need it later. But hang on...
That gets one light working. But you have more than one. Now you need another wire. == 14/3.
The problem is you need to have two wires going between all the lights: switched hot and neutral. And you need another wire, not connected to any lights, for hot to get to the switch. With only one light, we cheat a little (except that neutral should be in the switch box) because there is no "carry neutral along to the next light" since there is only one light. But with multiple lights that doesn't work. So now you replace the 14/2 from the first light through all the other lights to the switch with 14/3. That 14/3 will be black/white/red. As described above, whenever possible black = hot and white = neutral. So that leaves red = switched hot. Here we go:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/3 from first light to second light, at the first light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the other side of the light.
14/3 from first light to second light, at the second light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the previous cable's red switched hot and to the other side of the light. This actually means use a wire nut to connect the reds from the two cables plus a pigtail to the light.
All the later lights use that same setup: blacks together, whites together + light, reds together + light.
14/3 from last light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect red switched hot to lower right (= yellow according to the instructions)
- Cap the white neutral with a wire nut
Now you have all the lights working and you have neutral in the box in case you need it in the future.
add a comment |
According to the manual, for a single switch (as opposed to a a 3-way switch, which would require another wire and another (ordinary, non-dimmable) 3-way switch), the configuration is very simple (ignoring grounds, which should all be connected together everywhere):
- Top right screw = Black = Hot - this should go directly back to the panel
- Bottom right screw = Yellow = Switched Hot - this should go to the light(s)
- The "far side" of the lights goes to Neutral
With a single fixture this is straightforward:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/2 from light to switch at the light:
- Connect black hot to the first cable's black hot
- Connect white (="yellow") switched hot to the other side of the light.
14/2 from light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect white switched hot to lower right (= yellow according to the instructions)
Note that yellow is a typical "switched hot" color (could be red or blue or anything else except black, which is traditionally hot, white & gray, which are only neutral, or green, which is only ground). However, 14/2 cable only comes in black/white, so if you have the hot function in the cable then that gets black and switched hot or neutral gets white. Alternatively, if you have neutral function in the cable then that gets white and hot or switched hot gets black. So in this case, you use white as switched hot and then mark it with yellow tape to indicate that it is actually the switched hot.
This conveniently ignores that current code requires a neutral in the switch box, just in case you need it later. But hang on...
That gets one light working. But you have more than one. Now you need another wire. == 14/3.
The problem is you need to have two wires going between all the lights: switched hot and neutral. And you need another wire, not connected to any lights, for hot to get to the switch. With only one light, we cheat a little (except that neutral should be in the switch box) because there is no "carry neutral along to the next light" since there is only one light. But with multiple lights that doesn't work. So now you replace the 14/2 from the first light through all the other lights to the switch with 14/3. That 14/3 will be black/white/red. As described above, whenever possible black = hot and white = neutral. So that leaves red = switched hot. Here we go:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/3 from first light to second light, at the first light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the other side of the light.
14/3 from first light to second light, at the second light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the previous cable's red switched hot and to the other side of the light. This actually means use a wire nut to connect the reds from the two cables plus a pigtail to the light.
All the later lights use that same setup: blacks together, whites together + light, reds together + light.
14/3 from last light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect red switched hot to lower right (= yellow according to the instructions)
- Cap the white neutral with a wire nut
Now you have all the lights working and you have neutral in the box in case you need it in the future.
According to the manual, for a single switch (as opposed to a a 3-way switch, which would require another wire and another (ordinary, non-dimmable) 3-way switch), the configuration is very simple (ignoring grounds, which should all be connected together everywhere):
- Top right screw = Black = Hot - this should go directly back to the panel
- Bottom right screw = Yellow = Switched Hot - this should go to the light(s)
- The "far side" of the lights goes to Neutral
With a single fixture this is straightforward:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/2 from light to switch at the light:
- Connect black hot to the first cable's black hot
- Connect white (="yellow") switched hot to the other side of the light.
14/2 from light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect white switched hot to lower right (= yellow according to the instructions)
Note that yellow is a typical "switched hot" color (could be red or blue or anything else except black, which is traditionally hot, white & gray, which are only neutral, or green, which is only ground). However, 14/2 cable only comes in black/white, so if you have the hot function in the cable then that gets black and switched hot or neutral gets white. Alternatively, if you have neutral function in the cable then that gets white and hot or switched hot gets black. So in this case, you use white as switched hot and then mark it with yellow tape to indicate that it is actually the switched hot.
This conveniently ignores that current code requires a neutral in the switch box, just in case you need it later. But hang on...
That gets one light working. But you have more than one. Now you need another wire. == 14/3.
The problem is you need to have two wires going between all the lights: switched hot and neutral. And you need another wire, not connected to any lights, for hot to get to the switch. With only one light, we cheat a little (except that neutral should be in the switch box) because there is no "carry neutral along to the next light" since there is only one light. But with multiple lights that doesn't work. So now you replace the 14/2 from the first light through all the other lights to the switch with 14/3. That 14/3 will be black/white/red. As described above, whenever possible black = hot and white = neutral. So that leaves red = switched hot. Here we go:
14/2 from panel to light at the light:
- Connect white (neutral) to one side of the light.
- Pass black through to the next cable - it does not connect to the light.
14/3 from first light to second light, at the first light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the other side of the light.
14/3 from first light to second light, at the second light:
- Connect black hot to the previous cable's black hot
- Connect white neutral to the previous cable's white neutral and to one side of the light. This actually means use a wire nut to connect the whites from the two cables plus a pigtail to the light.
- Connect red switched hot to the previous cable's red switched hot and to the other side of the light. This actually means use a wire nut to connect the reds from the two cables plus a pigtail to the light.
All the later lights use that same setup: blacks together, whites together + light, reds together + light.
14/3 from last light to switch at the switch:
- Connect black hot to top right (= black according to the instructions)
- Connect red switched hot to lower right (= yellow according to the instructions)
- Cap the white neutral with a wire nut
Now you have all the lights working and you have neutral in the box in case you need it in the future.
answered 1 hour ago
manassehkatzmanassehkatz
7,9841032
7,9841032
add a comment |
add a comment |
So here are the wires you need.
- ground from supply to every lamp and switch. Ground must be green, green/yellow, or bare.
- neutral from supply to every lamp and switch. Neutral must be white.
- always-hot from the power supply to the switch. Always-hot is preferably black.
- switched-hot from the switch to every lamp. Switched-hot is ideally red, but can be black if the black wire is available.
As you can see, since power enters the opposite end from the switch, you need to carry "always-hot" all the way. You also need to carry "neutral" all the way. Then, if you want the lights to be switched, you need to carry switched-hot all the way back from the switch to the first lamp.
The lamp's hot wire is black. You can hook it to always-hot if you want it always-on, but if you want it switched, I suggest hooking it to switched hot.
So yeah, you need /3 cable starting at the first lamp.
add a comment |
So here are the wires you need.
- ground from supply to every lamp and switch. Ground must be green, green/yellow, or bare.
- neutral from supply to every lamp and switch. Neutral must be white.
- always-hot from the power supply to the switch. Always-hot is preferably black.
- switched-hot from the switch to every lamp. Switched-hot is ideally red, but can be black if the black wire is available.
As you can see, since power enters the opposite end from the switch, you need to carry "always-hot" all the way. You also need to carry "neutral" all the way. Then, if you want the lights to be switched, you need to carry switched-hot all the way back from the switch to the first lamp.
The lamp's hot wire is black. You can hook it to always-hot if you want it always-on, but if you want it switched, I suggest hooking it to switched hot.
So yeah, you need /3 cable starting at the first lamp.
add a comment |
So here are the wires you need.
- ground from supply to every lamp and switch. Ground must be green, green/yellow, or bare.
- neutral from supply to every lamp and switch. Neutral must be white.
- always-hot from the power supply to the switch. Always-hot is preferably black.
- switched-hot from the switch to every lamp. Switched-hot is ideally red, but can be black if the black wire is available.
As you can see, since power enters the opposite end from the switch, you need to carry "always-hot" all the way. You also need to carry "neutral" all the way. Then, if you want the lights to be switched, you need to carry switched-hot all the way back from the switch to the first lamp.
The lamp's hot wire is black. You can hook it to always-hot if you want it always-on, but if you want it switched, I suggest hooking it to switched hot.
So yeah, you need /3 cable starting at the first lamp.
So here are the wires you need.
- ground from supply to every lamp and switch. Ground must be green, green/yellow, or bare.
- neutral from supply to every lamp and switch. Neutral must be white.
- always-hot from the power supply to the switch. Always-hot is preferably black.
- switched-hot from the switch to every lamp. Switched-hot is ideally red, but can be black if the black wire is available.
As you can see, since power enters the opposite end from the switch, you need to carry "always-hot" all the way. You also need to carry "neutral" all the way. Then, if you want the lights to be switched, you need to carry switched-hot all the way back from the switch to the first lamp.
The lamp's hot wire is black. You can hook it to always-hot if you want it always-on, but if you want it switched, I suggest hooking it to switched hot.
So yeah, you need /3 cable starting at the first lamp.
answered 1 hour ago
HarperHarper
69.4k346140
69.4k346140
add a comment |
add a comment |
You need 14/3 between the lights
The reason why the lights are stuck ON is because they were wired directly between always-hot and neutral. Since you need to bring switched-hot back to all the lights in order for the switch to control them, you'll need to replace the 14/2 between the lights with 14/3.
add a comment |
You need 14/3 between the lights
The reason why the lights are stuck ON is because they were wired directly between always-hot and neutral. Since you need to bring switched-hot back to all the lights in order for the switch to control them, you'll need to replace the 14/2 between the lights with 14/3.
add a comment |
You need 14/3 between the lights
The reason why the lights are stuck ON is because they were wired directly between always-hot and neutral. Since you need to bring switched-hot back to all the lights in order for the switch to control them, you'll need to replace the 14/2 between the lights with 14/3.
You need 14/3 between the lights
The reason why the lights are stuck ON is because they were wired directly between always-hot and neutral. Since you need to bring switched-hot back to all the lights in order for the switch to control them, you'll need to replace the 14/2 between the lights with 14/3.
answered 1 hour ago
ThreePhaseEelThreePhaseEel
31.5k114993
31.5k114993
add a comment |
add a comment |
That’s what I was afraid of. Looks like I’ll be practicing my electrical wiring skills some more
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
add a comment |
That’s what I was afraid of. Looks like I’ll be practicing my electrical wiring skills some more
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
add a comment |
That’s what I was afraid of. Looks like I’ll be practicing my electrical wiring skills some more
That’s what I was afraid of. Looks like I’ll be practicing my electrical wiring skills some more
answered 42 mins ago
prchick1984prchick1984
61
61
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
add a comment |
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
You can add additional details as part of your original question. Don't add an answer to your own question, unless you have an actual answer (which sometimes happens). Also, take the tour
– manassehkatz
41 mins ago
add a comment |
Thanks for contributing an answer to Home Improvement Stack Exchange!
- Please be sure to answer the question. Provide details and share your research!
But avoid …
- Asking for help, clarification, or responding to other answers.
- Making statements based on opinion; back them up with references or personal experience.
To learn more, see our tips on writing great answers.
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
var $window = $(window),
onScroll = function(e) {
var $elem = $('.new-login-left'),
docViewTop = $window.scrollTop(),
docViewBottom = docViewTop + $window.height(),
elemTop = $elem.offset().top,
elemBottom = elemTop + $elem.height();
if ((docViewTop elemBottom)) {
StackExchange.using('gps', function() { StackExchange.gps.track('embedded_signup_form.view', { location: 'question_page' }); });
$window.unbind('scroll', onScroll);
}
};
$window.on('scroll', onScroll);
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
StackExchange.ready(
function () {
StackExchange.openid.initPostLogin('.new-post-login', 'https%3a%2f%2fdiy.stackexchange.com%2fquestions%2f157184%2flights-won-t-work-on-dimmer%23new-answer', 'question_page');
}
);
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
var $window = $(window),
onScroll = function(e) {
var $elem = $('.new-login-left'),
docViewTop = $window.scrollTop(),
docViewBottom = docViewTop + $window.height(),
elemTop = $elem.offset().top,
elemBottom = elemTop + $elem.height();
if ((docViewTop elemBottom)) {
StackExchange.using('gps', function() { StackExchange.gps.track('embedded_signup_form.view', { location: 'question_page' }); });
$window.unbind('scroll', onScroll);
}
};
$window.on('scroll', onScroll);
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
var $window = $(window),
onScroll = function(e) {
var $elem = $('.new-login-left'),
docViewTop = $window.scrollTop(),
docViewBottom = docViewTop + $window.height(),
elemTop = $elem.offset().top,
elemBottom = elemTop + $elem.height();
if ((docViewTop elemBottom)) {
StackExchange.using('gps', function() { StackExchange.gps.track('embedded_signup_form.view', { location: 'question_page' }); });
$window.unbind('scroll', onScroll);
}
};
$window.on('scroll', onScroll);
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
var $window = $(window),
onScroll = function(e) {
var $elem = $('.new-login-left'),
docViewTop = $window.scrollTop(),
docViewBottom = docViewTop + $window.height(),
elemTop = $elem.offset().top,
elemBottom = elemTop + $elem.height();
if ((docViewTop elemBottom)) {
StackExchange.using('gps', function() { StackExchange.gps.track('embedded_signup_form.view', { location: 'question_page' }); });
$window.unbind('scroll', onScroll);
}
};
$window.on('scroll', onScroll);
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
It sounds like maybe you need neutral - and therefore 14/3 - at the dimmer, in which case it maybe should have been 14/3 the whole way. But not very clear. Please provided, if you can: model # of dimmer switch, picture of wiring at last light (14/2 & 14/3), picture of wiring at dimmer switch.
– manassehkatz
2 hours ago
The switch is Halo LED SAL06P. I have the neutral unconnected since the switch says it doesn’t need a neutral with the black wire on top and red wire on bottom of the right hand side. From the switch, it’s to the last light in the chain where I have the neutrals together, the grounding together, the red to the light and the black from the incoming 14/2 and 14/3 together like I’ve seen in some diagrams online. All the other lights are setup so that all the whites are together, blacks are together, and grounding together.
– prchick1984